[HamWAN PSDR] [Netops] VOTE: 4 12V / 119Ah AGM batteries & DC PDU for Gold Mtn

rob at nr3o.com rob at nr3o.com
Thu Mar 22 11:33:17 PDT 2018


Nice – thanks for the update sir.

 

Cheers,

Rob

 

From: PSDR <psdr-bounces at hamwan.org> On Behalf Of Nigel Vander Houwen
Sent: Thursday, March 22, 2018 11:32 AM
To: Puget Sound Data Ring <psdr at hamwan.org>
Cc: netops at hamwan.org
Subject: Re: [HamWAN PSDR] [Netops] VOTE: 4 12V / 119Ah AGM batteries & DC PDU for Gold Mtn

 

HamWAN has approximately $2800 in the account and no debt presently, which will cover this Gold purchase pending approval, and the outstanding repair items needed for Haystack.

 

Nigel





On Mar 22, 2018, at 09:17, Rob Salsgiver <rob at nr3o.com <mailto:rob at nr3o.com> > wrote:

 

How’s the old bank balance these days?

 

Cheers,

Rob

 

From: PSDR [ <mailto:psdr-bounces at hamwan.org> mailto:psdr-bounces at hamwan.org] On Behalf Of Bart Kus
Sent: Wednesday, March 21, 2018 11:02 PM
To: Darcy Buskermolen; Puget Sound Data Ring
Cc:  <mailto:netops at hamwan.org> netops at hamwan.org
Subject: Re: [HamWAN PSDR] [Netops] VOTE: 4 12V / 119Ah AGM batteries & DC PDU for Gold Mtn

 

Bank should be ~5.7kWh.  3 sectors up there and 3 NetMetal modems, as well as a 900MHz modem and a CRS125 switch.  The sectors should take about 5.5W each, the NetMetals, 900MHz and CRS125 weren't measured but let's assume 10W each there.  So that looks like 65W total to me, for a runtime of ~88 hours, or 3.7 days.  And oh yeah, the PDU draws a little too.  We can also do load-shedding manually during an outage.

--Bart




On 3/21/2018 5:41 PM, Darcy Buskermolen wrote:

My question would be, what kind of runtime will this proposal provide ?

 

 

 

Sent on the go, from somewhere other than here.

 

-------- Original message --------

From: Doug Kingston  <mailto:dpk at randomnotes.org> <dpk at randomnotes.org>

Date: 2018-03-21 17:39 (GMT-08:00) 

To: Puget Sound Data Ring  <mailto:psdr at hamwan.org> <psdr at hamwan.org>

Cc:  <mailto:netops at hamwan.org> netops at hamwan.org

Subject: Re: [HamWAN PSDR] VOTE: 4 12V / 119Ah AGM batteries & DC PDU for Gold Mtn 

 

As a donating member and representing the ACS COMT team, I'll +1 Bart's proposal.

 

-Doug-

KD7DK

 

On Wed, Mar 21, 2018 at 12:36 PM, Bart Kus < <mailto:me at bartk.us> me at bartk.us> wrote:

Hello,

As some of you have noticed, Gold Mtn has been having power issues the last couple of months.  To mitigate this, we'd like to convert it onto a DC battery bank system.  This requires 2 new item purchases:

1) A 24V battery bank to run the site for a few days in case of power outage
2) A DC PDU (Power Distribution Unit / PoE injector) to control and monitor power usage

The battery bank is $500 for 240Ah @ 24V.  The PDU is $231.03.  The total for this spending request is therefore $731.03.

Only directors may vote to approve the spend, but anyone is welcome to comment with input during the next 24 hours.

Thanks,

--Bat

_______________________________________________
PSDR mailing list
 <mailto:PSDR at hamwan.org> PSDR at hamwan.org
 <http://mail.hamwan.net/mailman/listinfo/psdr> http://mail.hamwan.net/mailman/listinfo/psdr

 







_______________________________________________
Netops mailing list
 <mailto:Netops at hamwan.org> Netops at hamwan.org
 <http://mail.hamwan.net/mailman/listinfo/netops> http://mail.hamwan.net/mailman/listinfo/netops

 

_______________________________________________
PSDR mailing list
 <mailto:PSDR at hamwan.org> PSDR at hamwan.org
 <http://mail.hamwan.net/mailman/listinfo/psdr> http://mail.hamwan.net/mailman/listinfo/psdr

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://mail.hamwan.net/pipermail/psdr/attachments/20180322/2b577f5b/attachment.html>


More information about the PSDR mailing list